Damper Pressure Drop

Post by crroda »

In designing duct systems, it is helpful to account for all of the system component pressure drops. What is a reasonable estimate for the pressure drop (in. w.c.) or equivalent length (ft.) for a round damper :?:
Eric K.

Re: Damper Pressure Drop

Post by Eric K. »

The design of the URD dampers provides very little resistance to air flow and posses a low pressure drop. The pressure drop across a URD damper will be no higher than 0.005-0.01 inches of H20 with an approach velocity of 700-900 FPM.

Eric
crroda
Posts: 5
Joined: Sun Mar 07, 2010 6:49 pm

Re: Damper Pressure Drop

Post by crroda »

that pressure drop is hardly worth any concern. Thanks for your fast reponse.