Humidifer Wiring into ST-2D panel

Post your questions and comments here.
Post Reply
jcalab8482
Posts: 1
Joined: Sun Jan 03, 2010 1:53 pm

Humidifer Wiring into ST-2D panel

Post by jcalab8482 »

I Have a 1999 EWC ST-2C Ultra Zone Control Panel with 2 zones running a Hallmark oil fired hot air furnace. My question is - Can I wire my Hamilton 10HF Furnace Humidifier into the 24 volt terminals in the Ultra Zone panel so that the humidifier comes on when the Furnace fan is running. I currently have it wired into a 24 transformer on my furnace. Thanks.
Eric K.

Re: Humidifer Wiring into ST-2D panel

Post by Eric K. »

To run the humidifier when the furnace fan is running, a current sensing relay (Model APD) needs to be added to the circuit. Refer to the following link for further information.

http://www.ewccontrols.com/acrobat/090377a0122.pdf

Eric K.
Post Reply