dual fuel help

Post your questions and comments here.
Post Reply
jtk111264
Posts: 1
Joined: Fri Nov 09, 2012 8:20 pm

dual fuel help

Post by jtk111264 »

I have BM3000 plus board with a rheem heat pump and a gas furnace backup im having a hard time to get my furnace to start running when the temp drops below 35 my heat pump is still running instead of my gas furnace. I have a oas connected to the board and set for around 35 degrees any help would be great. Thank
Pcyrana

Re: dual fuel help

Post by Pcyrana »

Can you tell me how you have all of your dip switches set.
Starting from the top of the bank with the number one switch, simply tell me whether the switch is set to the left or to the right.
Also, do you have a voltmeter?
I would like to check the resistance value across the OAS itself to see if it is functioning properly.
The wires should be disconnected from the OAS terminals on the board and resistance should be checked across the wires themselves.
Take note of the outside temperature at the time you check.