St-2e

Post your questions and comments here.
Post Reply
Kvothee531
Posts: 1
Joined: Mon Aug 03, 2026 9:07 pm

St-2e

Post by Kvothee531 »

Hi, I just moved into a new ( to me) home that was built back in '06. It has the st-2e board there are 2 thermostats on the second floor, one wired as a master (rwygob) and one with just the three wires. On the main floor there is another thermostat wired as a master. In the basement (finished) there is another wired as a slave. I have no idea how this zoning makes sense. There are two ac/air units outside, obviously no heat pump (oil heat and central air). I was planning to upgrade the board so I can start using smart thermostats but I don't want to have to rewire the house. Any ideas?
Steven W.
Posts: 140
Joined: Tue Jun 25, 2019 9:13 am

Re: St-2e

Post by Steven W. »

You will need to replace your ST-2E zone board with the NCM-3z. NO new wiring if you are not putting a WIFI stat on the 2nd zone. If you are planning on putting a WIFI stat on zone 2 then "Yes" you will need to run more then 3 wires to that zone.
Steven R. Weisneck
Chief Technician
Tel: (732) 446-3110 Ext. #461
www.ewccontrols.com
sweisneck@ewccontrols.com
Post Reply