NCM-300 Heat Pump with Aux Heat Furnace

Post your questions and comments here.
Post Reply
petrasvainiusII
Posts: 1
Joined: Sun Oct 05, 2025 12:00 pm

NCM-300 Heat Pump with Aux Heat Furnace

Post by petrasvainiusII »

What are the correct settings for the NCM-300 running two zones powered by an American Standard Heat Pump with propane auxiliary heat?

As the system stand, it appears the O/B is constantly energized.
Steven W.
Posts: 130
Joined: Tue Jun 25, 2019 9:13 am

Re: NCM-300 Heat Pump with Aux Heat Furnace

Post by Steven W. »

The NCM 300 is not a duel fuel zone board. You need to go with a BMPlus-3z. There is a workaround if you have heatpump stats and you set them to Duel Fuel (now you are letting the stat's control your staging between heatpump and backup heat).
Steven R. Weisneck
Chief Technician
Tel: (732) 446-3110 Ext. #461
www.ewccontrols.com
sweisneck@ewccontrols.com
Post Reply