What are the correct settings for the NCM-300 running two zones powered by an American Standard Heat Pump with propane auxiliary heat?
As the system stand, it appears the O/B is constantly energized.
NCM-300 Heat Pump with Aux Heat Furnace
-
- Posts: 1
- Joined: Sun Oct 05, 2025 12:00 pm
Re: NCM-300 Heat Pump with Aux Heat Furnace
The NCM 300 is not a duel fuel zone board. You need to go with a BMPlus-3z. There is a workaround if you have heatpump stats and you set them to Duel Fuel (now you are letting the stat's control your staging between heatpump and backup heat).