NCM300 - Maximum URD and SID Dampers

Post your questions and comments here.
Post Reply
ajheat
Posts: 2
Joined: Fri Jan 07, 2011 10:46 pm

NCM300 - Maximum URD and SID Dampers

Post by ajheat »

What is the maximum number of URD and/or SID dampers that can be connect to one zone of the NCM300 before you need to use an auxiliary relay with an additional transformer?
Eric K.

Re: NCM300 - Maximum URD and SID Dampers

Post by Eric K. »

A maximum of 12 per zone and 25 total across all zones. The largest transformer you can use is a 24vac 60VA transformer.

Eric
ajheat
Posts: 2
Joined: Fri Jan 07, 2011 10:46 pm

Re: NCM300 - Maximum URD and SID Dampers

Post by ajheat »

Wow. The NCM300 can actually handle enough current to control up to 12 URD or SID dampers on one zone. I have to assume then that the URD and SID dampers must have very low current drive motors.

I'll have 10 dampers on two zones for a total of 20 dampers in the system and I'll use a 24Vac 60AV transformer.

Thanks.