UZC Problem

Post your questions and comments here.
Post Reply
Airteam
Posts: 8
Joined: Sat Jun 20, 2009 12:38 pm

UZC Problem

Post by Airteam »

I have one in my home and I noticed that with the 50% rule in the "on" position on the board it was not activating Y2 which energizes my 2 stage compressor. I am using 3 zones and all 3 thermostats were calling. I have tried resetting the board. I have the timer set to off.
Airteam
Posts: 8
Joined: Sat Jun 20, 2009 12:38 pm

Re: UZC Problem

Post by Airteam »

Well I have solved this problem but I dont know if the board is suppose to work this way. If I move the dial below the 7 minute mark on the staging dial, stage 2 never kicks in. Set it on the high side of 7 and it works.
John B.
Posts: 30
Joined: Fri Mar 13, 2009 8:57 am

Re: UZC Problem

Post by John B. »

Dear Sir,

I'm sorry for the late response...You have indeed figured out the problem.....Below 7 there is no value....Anything below 7 = OFF

Thank You so very much!

John
John Brown :geek:
Airteam
Posts: 8
Joined: Sat Jun 20, 2009 12:38 pm

Re: UZC Problem

Post by Airteam »

The value of the setting of the RA/DA switch should be stressed with bright colors, flags and balloons. :lol: