NCM300 upgrade

Post by jbis »

Just like this thread viewtopic.php?f=4&t=404 I am installing Nest thermostats and need to upgrade to the NCM300 from the ST-3. I have a question on the wiring. My zone 1 thermostat has both a blue and brown wire hooked up to separate B and O connections. (zone 2 & 3 are simple 3 wire (red, white, yellow) connections) The ST-3 also has these O and B connections coming into it, however, going out to the furnace, they are not even connected to the board OR the furnace. So, is the zone panel doing something with these connections or can I take the blue wire and feed the thermostats a C wire?
Last edited by jbis on Thu Mar 07, 2013 11:40 am, edited 1 time in total.
jbis
Posts: 3
Joined: Wed Mar 06, 2013 10:57 am
Location: Upstate NY

Re: NCM300 upgrade

Post by jbis »

Here's the furnace shot
Last edited by jbis on Thu Mar 07, 2013 11:39 am, edited 1 time in total.
Erik W.
Posts: 117
Joined: Fri Dec 07, 2012 11:23 am
Location: Englishtown, NJ
Contact:

Re: NCM300 upgrade

Post by Erik W. »

You do not need to hook the O or the B anymore. Your old panel required it because it was a master slave but the NCM-300 is not and only requires an O or a B if you have a heat pump, you can use one of those wires as your common wire .

Erik
jbis
Posts: 3
Joined: Wed Mar 06, 2013 10:57 am
Location: Upstate NY

Re: NCM300 upgrade

Post by jbis »

Excellent! Thank you!