I have the EWC 3000 Plus Controller.
When Zone 1 is cooled off and the thermostat stops calling for cool air, should I expect the zone 1 damper to close? If yes, is there a delay in the damper closing? Or does the damper just stay open until the other zone calls?
Expected Damper Operation
Re: Expected Damper Operation
Jim,
Was Zone 1 the only zone calling at the time? When there is no longer a demand for heating or cooling, the equipment will shut down and the control panel will default all zones Open.
Eric
Was Zone 1 the only zone calling at the time? When there is no longer a demand for heating or cooling, the equipment will shut down and the control panel will default all zones Open.
Eric
Re: Expected Damper Operation
Oh okay, the question was answered then. Both zones were opened when the system stopping calling for cool in both zones. Thanks!