I had have the EWC control panel and the Zone 1 Honeywell thermostat died. I purchased a Honeywell RTH7500. Will this thermostat work with it? If so, how is it wired to work correctly?
Re: EWC-St-2D
Unfortunately that RTH7500 thermostat will not work for you on Zone One.
Your Zone One thermostat needs to have a separate O and separate B terminal.
The RTH7500 does not meet those requirements.
If you want a simple non-programmable thermostat you can use the Honeywell TH3110D.
If you would like a programmable thermostat you can go with the Honeywell TH4110D.
Both the O and B terminals need to be wired to the board separately.