ND Dampers partially open?

Post your questions and comments here.
Post Reply
Bookman
Posts: 5
Joined: Wed Sep 07, 2011 5:09 pm

ND Dampers partially open?

Post by Bookman »

Can ND dampers be set to remain partially open when its zone is not calling, then open completely when the zone calls?
Pcyrana

Re: ND Dampers partially open?

Post by Pcyrana »

Yes the ND dampers could be set the way you described. You would want to utilize the end stop adjustments to allow for a particular amount of leakage. I have attached a document that shows how to use these stops.
You want to adjust the one with the "1" next to it. That is the stop that prevents the damper from closing 100%.