UZC Problem in Cool Mode

Post your questions and comments here.
Post Reply
jedwilli
Posts: 2
Joined: Sun Jun 28, 2009 9:13 am

UZC Problem in Cool Mode

Post by jedwilli »

I have a UZVC4 that worked perfectly through the winter. Four thermostates with four dampers worked perfectly.

In cool mode however I have a problem. If two or more zones are requesting for cool those zones open and the system cools correctly.

However if zone 1 request for cooling by itself, the emergency led comes on, the system goes into high fan speed and blows warm air. I swapped zones 1 and 2 just to verify this wasn't a wiring issue or thermostat issue and the problem stayed with zone 1. The system fan control is set to all - at this point I'm clueless. Any ideas?

-jw
Airteam
Posts: 8
Joined: Sat Jun 20, 2009 12:38 pm

Re: UZC Problem in Cool Mode

Post by Airteam »

Check the position of the RA/DA micro switch. It should be in the DA position(to the right). #5 on the bottom bank of switches

Hold down reset for 5 seconds if you change it.
John B.
Posts: 30
Joined: Fri Mar 13, 2009 8:57 am

Re: UZC Problem in Cool Mode

Post by John B. »

Airteam is correct Jedwilli....The RA/DA dip switch must be set to DA or it will attempt to perform a de-humidify function...because there is no control connected to the Aux R input terminal.

Thanks Airteam!
John Brown :geek:
jedwilli
Posts: 2
Joined: Sun Jun 28, 2009 9:13 am

Re: UZC Problem in Cool Mode

Post by jedwilli »

I will try this now! Thanks!