Fan runs after shutdown on Ultra-Zone panel
Fan runs after shutdown on Ultra-Zone panel
Hi everyone, I’m using an EWC Ultra-Zone control panel with a multi-zone setup, and I’ve noticed that the system fan continues to run for about 3–5 minutes after the thermostat reaches the set temperature and shuts off the cooling. Is this normal behavior for the panel, or could it be related to a specific setting like purge or fan delay?Infinite Craft I checked the basic wiring and thermostat settings, but nothing seems unusual. I’d appreciate any guidance on what to check or adjust to fix this.
Re: Fan runs after shutdown on Ultra-Zone panel
It is normal behavior for your fan purge. You can lower it or turn it off.