Hi,
I’m trying to replace the existing thermostats with Ecobees on a zoned system. When I looked at the wiring at the thermostat, there were four wires (W, R, G, Y), no C wire though. Looking at the zone controller the C terminal is empty on the Zones 1 and 2 Tstats. There appears to be an extra wire that wasn’t used which I could use to connect the C wire on the zone controller to the c terminal on my Ecobee but I need to double check if it really is there. I also have the PEK power adapter but that seems silly if there’s an extra wire. Finally, the NCM300 is powered by a stand alone transformer. There’s no C wire connection between the zone controller and the HVAC unit. Which is the right answer? Is the standalone transformer enough to power to ecobees via the c terminal or using the PEK adapter?
Thanks, I included a couple photos in case it helps.
Wiring Ecobee enhanced on NCM300 no C wire
Wiring Ecobee enhanced on NCM300 no C wire
You do not have the required permissions to view the files attached to this post.
Re: Wiring Ecobee enhanced on NCM300 no C wire
You can use the "G" green wire as your "C" Common wire. Your fan will still run when it is needed.
Steven R. Weisneck
Technical Engineer
Tel: (732) 446-3110 Ext. #461
www.ewccontrols.com
sweisneck@ewccontrols.com
Technical Engineer
Tel: (732) 446-3110 Ext. #461
www.ewccontrols.com
sweisneck@ewccontrols.com
Re: Wiring Ecobee enhanced on NCM300 no C wire
Thanks Stephen. If I want manual control of the fan (to say circulate air 15min/ hr), which I believe I will lose if I use the G wire as C, can I use the blue wire and connect C on the thermostat to C on the zone controller? My understanding is that the dedicated 40VA transformer has enough power to power the two dampers in my system. I estimate about 35VA peak load at the most.
Re: Wiring Ecobee enhanced on NCM300 no C wire
That is correct if you use the G wire as the common wire then you will lose the ability to run your fan manually. Yes 40VA transformer is more then what you will need.
Steven R. Weisneck
Technical Engineer
Tel: (732) 446-3110 Ext. #461
www.ewccontrols.com
sweisneck@ewccontrols.com
Technical Engineer
Tel: (732) 446-3110 Ext. #461
www.ewccontrols.com
sweisneck@ewccontrols.com
Re: Wiring Ecobee enhanced on NCM300 no C wire
Thanks a lot Stephen. Installed the thermostats today and tested all the functionality. They work great. Turns out the blue wire was available so all I did is connect it to the C terminal at both ends. Thanks for the advice.