SAS Sensor heating temprerature

Post by t0lkman »

Hello there,

What is the average heating temperature the supply sensor should show?
I have 5 ton Daikin Fit system, and SAS sensor on maximum heating shows 90F is it normal?

Indoor thermostat set on 71, but never reaches 71F only 69 when outdoor temperature is 40-43F (house is 2 floor, 2200 sqft)

Thanks!
Steven W.
Posts: 116
Joined: Tue Jun 25, 2019 9:13 am

Re: SAS Sensor heating temprerature

Post by Steven W. »

The SAS is a 10.5K that's right around 75 degrees. I include on this forum how to test your SAS
You do not have the required permissions to view the files attached to this post.
Steven R. Weisneck
Technical Engineer
Tel: (732) 446-3110 Ext. #461
www.ewccontrols.com
sweisneck@ewccontrols.com
t0lkman
Posts: 8
Joined: Wed Nov 27, 2024 1:19 am

Re: SAS Sensor heating temprerature

Post by t0lkman »

Thank you! I tested and the SAS sensor is working perfectly. I now need to confirm what is the expectation from 3.5 ton hear pump to produce heat? (No furnace and no heating strips)

Based on your experience how hot air could be produced by heat pump on average?