S2000 control wiring

Post your questions and comments here.
Post Reply
LazyEyeMcfly
Posts: 1
Joined: Thu Jan 06, 2011 10:02 pm

S2000 control wiring

Post by LazyEyeMcfly »

I feel like giving the humidifier fan control could hurt my heating operation. Isn't it enough to add a current sensing relay so it at least has a safety proving the fan?? I get it that it wants 170deg before the fan comes on. I guess the furnace board should still bring the fan on when it is supposed to regardless of the G being interrupted by the humidifer board. Any problems here or should i just have faith in the diagram??
Thanks....
Eric K.

Re: S2000 control wiring

Post by Eric K. »

The terminals G1 & G2 are Normally Closed, therefore allowing a fan call from the thermostat to pass through and operate normally.

The terminals R & G2 are Normally Opened and close when there is a demand for humidity, allowing the humidifier to operate independently of the heating cycle. Also during a demand for humidity, the G1 & G2 terminals are opened, which prevents a back feed through the thermostat inadvertently operating the compressor.