Old EWC unit 3 wire thermostat

Post your questions and comments here.
Post Reply
slieblich
Posts: 2
Joined: Sun Apr 07, 2013 2:32 pm

Old EWC unit 3 wire thermostat

Post by slieblich »

have a 3 wire EWC thermostat,part of 2 zone system with damper control board from EWC. Installation 1990. There is a remote switch for heat/ac/off along with fan auto/on
I'd like to change to a smart thermostat, and note 3 wires in my thermostat: Y6; R5; W4
are there equivalents of these wires to what is the R, fan and Heat wire? I assume the remote switcher causes the heat wire to change to AC wire when that switch is thrown.
Erik W.
Posts: 117
Joined: Fri Dec 07, 2012 11:23 am
Location: Englishtown, NJ
Contact:

Re: Old EWC unit 3 wire thermostat

Post by Erik W. »

Your remote switch does not switch the heat wire to a/c when the switch is thrown it actually energizes either your O or B terminal which switches the thermostats between heat and cool. R is 24 volt hot, Y is for cooling and W is for heating. You do not have a fan wire hooked up, and it is not needed because both your indoor and outdoor units will bring on the fan themselves upon a call for heat or cool. You only need a G wire for continuous fan only operation. When installing your new smart thermostats you are going to only need to connect the same three wires, a fourth wire can be added to the common terminal to run the thermostats on 24VAC instead of battery power.

Erik
slieblich
Posts: 2
Joined: Sun Apr 07, 2013 2:32 pm

Re: Old EWC unit 3 wire thermostat

Post by slieblich »

Thank you for the explanation and info; Appreciate it!
Not sure what is meant by the O and B terminal, but I assume I need to bring in a common wire since the Nest doesn't have a battery. Does that need to come off the same 24v transformer as is serving the R wire? I see 2 transformers on my air handler.
thanks again.
Stu
Erik W.
Posts: 117
Joined: Fri Dec 07, 2012 11:23 am
Location: Englishtown, NJ
Contact:

Re: Old EWC unit 3 wire thermostat

Post by Erik W. »

The board is supplying the power to the thermostats from the R terminal on the thermostat terminal blocks and you will be hooking up your common wire to the C terminal on the board at the thermostat terminal block, you do not need to do anything with the transformer in your unit.
alfredalfred
Posts: 1
Joined: Tue May 03, 2016 3:26 am

Re: Old EWC unit 3 wire thermostat

Post by alfredalfred »

There are equivalents of these wires to what is the R, fan and Heat wire? I assume the remote switcher causes the heat wire to change to AC wire when that switch is thrown???
waleeed
Paul Z.
Posts: 216
Joined: Thu Dec 08, 2011 3:05 pm

Re: Old EWC unit 3 wire thermostat

Post by Paul Z. »

Yes you are correct.