EWC-ST-3C Damper Motor Halfway?
EWC-ST-3C Damper Motor Halfway?
Our upstairs has been out-of-control hot. Took a look at how the dampers operated, and it appears that the upstairs damper motor stops halfway between open and closed. If I give it a little push, it finishes closing. I checked - the dampers themselves are fine, and move easily. This installation is from 1994. The dampers should never be halfway, correct? Can I assume I need a new motor, or is it possible to service it (oil?)? I don't mind getting a contractor, but only if I can't do it myself. Thanks for any advice!
Re: EWC-ST-3C Damper Motor Halfway?
Yes it sound like you need a new motor. Give a call and we can help you better with just a few questions. 1-800 446 3110 X490
Re: EWC-ST-3C Damper Motor Halfway?
Thanks, Paul. I'll call later today.
Re: EWC-ST-3C Damper Motor Halfway?
Gotta mention - I checked the third damper, and it's not moving at all. Only one good motor left. BUT, they're 22 years old, so not shocked. Thanks for your response and your help today! I know what I need to do now.
Re: EWC-ST-3C Damper Motor Halfway?
LAST question - is the MAN motor the same as "standard (power open/power closed)" motor that comes with new ND dampers? If so, any reason I can't just order this online through the estore? THANKS AGAIN!
Re: EWC-ST-3C Damper Motor Halfway?
No motor actuators are different.