I have a EWC -ST3D controlling 3 zones. I have oil furnace hot air heating and american standard central airconditioning. I want to replace the dial thermostat with a honeywell TH 4110D programmable thermostat on Zone 1 since it is the compatible thermostat per the manual. The wires coming in Zone 1 are W, Y, R1, O, B and G from the EWC-ST3d panel. The terminals available on the thermostat are: W, Y, G, O, Rc, R, B and C. Can you suggest the wiring diagram to connect the wires to the thermostat?
Thanks You.
-Harsh
Honeywell TH 4110D wiring question
Re: Honeywell TH 4110D wiring question
Harsh,
Match terminal to terminal. Also, jumper the R and Rc on the thermostat and connect to R1 on the zone panel. Do not connect the C, use the batteries to power the thermostat.
Eric
Match terminal to terminal. Also, jumper the R and Rc on the thermostat and connect to R1 on the zone panel. Do not connect the C, use the batteries to power the thermostat.
Eric
Re: Honeywell TH 4110D wiring question
Thank you!