UT-3000 showing Emergency Heat with a Gas only furnace

Post your questions and comments here.
Post Reply
innoman
Posts: 6
Joined: Wed Aug 21, 2013 7:38 pm

UT-3000 showing Emergency Heat with a Gas only furnace

Post by innoman »

Is it normal for a gas only setup to have the Emergency Heat light lit on the UT-3000? It hasn't been before today that I have noticed. I am on 1.17.
Erik W.
Posts: 117
Joined: Fri Dec 07, 2012 11:23 am
Location: Englishtown, NJ
Contact:

Re: UT-3000 showing Emergency Heat with a Gas only furnace

Post by Erik W. »

What other lights were lit on the ut 3000 along with the emergency heat LED light?

Erik Wnoroski
EWC Controls, Inc.
385 State Route 33
Englishtown, NJ 07726
800-446-3110 ext 483
innoman
Posts: 6
Joined: Wed Aug 21, 2013 7:38 pm

Re: UT-3000 showing Emergency Heat with a Gas only furnace

Post by innoman »

Heat / B and Zones 1,2,3 (Sometimes just one of two of the zones. Also, sometimes the dry relay light is on.

It also appears that the system will not move to the 2nd stage in this scenario. Even if the demand for heat is high in all 3 zones.