Humidifer Wiring into ST-2D panel
-
- Posts: 1
- Joined: Sun Jan 03, 2010 1:53 pm
Humidifer Wiring into ST-2D panel
I Have a 1999 EWC ST-2C Ultra Zone Control Panel with 2 zones running a Hallmark oil fired hot air furnace. My question is - Can I wire my Hamilton 10HF Furnace Humidifier into the 24 volt terminals in the Ultra Zone panel so that the humidifier comes on when the Furnace fan is running. I currently have it wired into a 24 transformer on my furnace. Thanks.
Re: Humidifer Wiring into ST-2D panel
To run the humidifier when the furnace fan is running, a current sensing relay (Model APD) needs to be added to the circuit. Refer to the following link for further information.
http://www.ewccontrols.com/acrobat/090377a0122.pdf
Eric K.
http://www.ewccontrols.com/acrobat/090377a0122.pdf
Eric K.