Is the Honeywell 8110U programmable thermostat compatible with the EWC -ST-2B zone control?
We just had a new furnace installed and I asked the tech to replace the current thermostat (Honeywell 3110D) with the 8110U from our previous house. The main issue is that when the master thermostat (8110U) is set to off, it does not kill the functions of the slave thermostat. All other functions seem to operate normally.
I am trying to determine if the thermostat is incompatible or if the techs need to change a setting in the furnace (Lenox EL296V).
Thanks,
Marty
Honeywell 8110U
Re: Honeywell 8110U
Marty,
That thermostat is not compatible for the master zone (zone 1) of you panel. You will need to purchase a thermostat with a separate o and b terminals, unfortunately the 8110U thermostat you have has a combined 0/b terminal.
Erik Wnoroski
EWC Controls, Inc.
385 State Route 33
Englishtown, NJ 07726
800-446-3110 ext 483
That thermostat is not compatible for the master zone (zone 1) of you panel. You will need to purchase a thermostat with a separate o and b terminals, unfortunately the 8110U thermostat you have has a combined 0/b terminal.
Erik Wnoroski
EWC Controls, Inc.
385 State Route 33
Englishtown, NJ 07726
800-446-3110 ext 483
Re: Honeywell 8110U
Thanks, Eric. I appreciate your reply.
Marty