I have Rheem RGFG-06EMCK furnace, RARL024 A/C Condenser and RHC-TST550CMMS communicating thermostat. I would like to create 2 zones and I see that UT-3000 Zone Control System is communicating. My question is will that zoning control work with the Rheem communicating thermostats?
If not is there any Zone Control System that is compatible with Rheem communicating thermostats (Comfort Control II).
Any help will be greatly appreciated.
Question about UT-3000 Zone Control System
Re: Question about UT-3000 Zone Control System
Those Rheem communicating thermostats are compatible with the UT 3000.
Erik Wnoroski
EWC Controls, Inc.
385 State Route 33
Englishtown, NJ 07726
800-446-3110 ext 483
Erik Wnoroski
EWC Controls, Inc.
385 State Route 33
Englishtown, NJ 07726
800-446-3110 ext 483
Re: Question about UT-3000 Zone Control System
That's very good news! I'm purchasing one. Now one more question - Can the second zone use none communicating thermostat? I already have communicating thermostat on the first zone.
Re: Question about UT-3000 Zone Control System
Yes, you can use one communicating thermostat in zone 1 and the rest can be 24 volt stats.
Erik Wnoroski
EWC Controls, Inc.
385 State Route 33
Englishtown, NJ 07726
800-446-3110 ext 483
Erik Wnoroski
EWC Controls, Inc.
385 State Route 33
Englishtown, NJ 07726
800-446-3110 ext 483