Sorry for the late response.
The Y and G connections are obviously the same. Your existing W wire will connect to the W1/B terminal on the NCM300. Your existing R wire will connect to the Rc terminal on the NCM300. (Rc & Rh are connected internally).
Let us know how it goes.
John
Search found 30 matches
- Wed May 25, 2016 11:29 am
- Forum: Help and Advice
- Topic: Upgrading from EWC-ST-2E to NCM300
- Replies: 1
- Views: 3487
- Tue Apr 28, 2015 10:23 am
- Forum: Help and Advice
- Topic: Ultra Talk 3000 communications
- Replies: 3
- Views: 19852
Re: Ultra Talk 3000 communications
Christopher, We appreciate your keen interest in the UT3000 and you are obviously quite knowledgeable. Answers to your questions are below. 1] can the UT-3000 handle true Modulating equipment and not just operate it as staged? YES 2] can EWC and i work together on my custom project so that I may int...
- Tue Apr 28, 2015 10:23 am
- Forum: Help and Advice
- Topic: Ultra Talk 3000 communications
- Replies: 3
- Views: 19852
Re: Ultra Talk 3000 communications
Christopher, We appreciate your keen interest in the UT3000 and you are obviously quite knowledgeable. Answers to your questions are below. 1] can the UT-3000 handle true Modulating equipment and not just operate it as staged? YES 2] can EWC and i work together on my custom project so that I may int...
- Tue Aug 17, 2010 1:18 pm
- Forum: Help and Advice
- Topic: Radio Frequency Interference from Controller
- Replies: 3
- Views: 8210
Re: Radio Frequency Interference from Controller
Tom, This zone product is quiet and we normally don't see this unless there is 1 or 2 expansion modules connected to it. Even then, it is minor. The main panel does not have a noisy switching power supply. Everything is pretty well contained on the processor. What kind of dampers do you have and how...
- Fri May 07, 2010 9:20 am
- Forum: Help and Advice
- Topic: The NEWS / ECW webinar
- Replies: 1
- Views: 7094
Re: The NEWS / ECW webinar
Sir,
Thank you for the kind words and we appreciate You and your Company.
Tell your Technicians to call EWC if they have any questions or need help when they are on a job site...On site Technicians get Priority Status when calling the Technical Support Hotline.
John Phillip Brown
Thank you for the kind words and we appreciate You and your Company.
Tell your Technicians to call EWC if they have any questions or need help when they are on a job site...On site Technicians get Priority Status when calling the Technical Support Hotline.
John Phillip Brown
- Mon Jun 29, 2009 1:21 pm
- Forum: Help and Advice
- Topic: Need Help!
- Replies: 1
- Views: 6527
Re: Need Help!
Rmendez, The problem you have described sounds like there may be a sticking zone damper (half open or half closed) or maybe a bypass damper sticking. It also sounds like the duct-work needs to be balanced.... The balancing cannot be performed until all dampers are confirmed to function correctly. If...
- Mon Jun 29, 2009 12:07 pm
- Forum: Help and Advice
- Topic: UZC Problem in Cool Mode
- Replies: 3
- Views: 8422
Re: UZC Problem in Cool Mode
Airteam is correct Jedwilli....The RA/DA dip switch must be set to DA or it will attempt to perform a de-humidify function...because there is no control connected to the Aux R input terminal.
Thanks Airteam!
Thanks Airteam!
- Fri Jun 26, 2009 10:27 am
- Forum: Help and Advice
- Topic: motors not moving
- Replies: 1
- Views: 7931
Re: motors not moving
Sir, If the LED on each MA-ND3 motor changes immediately but no movement of the actuator occurrs, then the motor has failed. If that is the case then the motors should be replaced. The correct replacement is a part #MA-ND4 or if you can't find it a part #MRK will also work.... I apologize for the in...
- Mon Jun 22, 2009 10:59 am
- Forum: Help and Advice
- Topic: My power bill
- Replies: 2
- Views: 8822
Re: My power bill
Thank You for the power consumption data.....Congratulations on lowering your energy bill....Are you able to determine how much of the difference can be attributed to the new Heat Pump and Zoning and how much was due to switching to Tankless LP to heat your water?
Best Regards,
John
Best Regards,
John
- Mon Jun 22, 2009 10:47 am
- Forum: Help and Advice
- Topic: UZC Problem
- Replies: 3
- Views: 9806
Re: UZC Problem
Dear Sir,
I'm sorry for the late response...You have indeed figured out the problem.....Below 7 there is no value....Anything below 7 = OFF
Thank You so very much!
John
I'm sorry for the late response...You have indeed figured out the problem.....Below 7 there is no value....Anything below 7 = OFF
Thank You so very much!
John