Search found 2 matches

by ajheat
Tue Jan 11, 2011 10:19 pm
Forum: Help and Advice
Topic: NCM300 - Maximum URD and SID Dampers
Replies: 2
Views: 8450

Re: NCM300 - Maximum URD and SID Dampers

Wow. The NCM300 can actually handle enough current to control up to 12 URD or SID dampers on one zone. I have to assume then that the URD and SID dampers must have very low current drive motors. I'll have 10 dampers on two zones for a total of 20 dampers in the system and I'll use a 24Vac 60AV ...
by ajheat
Fri Jan 07, 2011 11:00 pm
Forum: Help and Advice
Topic: NCM300 - Maximum URD and SID Dampers
Replies: 2
Views: 8450

NCM300 - Maximum URD and SID Dampers

What is the maximum number of URD and/or SID dampers that can be connect to one zone of the NCM300 before you need to use an auxiliary relay with an additional transformer?