Search found 3 matches

by tom3holer
Tue Aug 16, 2022 7:55 am
Forum: Help and Advice
Topic: 2 zones, one of which leaks when other is on
Replies: 2
Views: 2877

Update #2

I have found the problem. It indeed is not the vanes but the gap between the top of the valve assembly and the ductwork. The duct has a bulge right over the vane and all the air was escaping through that area. Also the valve is constructed 3/16" under size on both dimensions thus increasing the gap ...
by tom3holer
Mon Aug 15, 2022 11:54 am
Forum: Help and Advice
Topic: 2 zones, one of which leaks when other is on
Replies: 2
Views: 2877

Re: 2 zones, one of which leaks when other is on

I did remove the zone valve to see if a vanes were not working but it seems they are all rotating. They are not tight when in the closed position which may be contributing the bypass air. The problem is there is no service manual listed even under the retired section for a MA-ND zone valve. Does ...
by tom3holer
Sat Aug 13, 2022 12:23 pm
Forum: Help and Advice
Topic: 2 zones, one of which leaks when other is on
Replies: 2
Views: 2877

2 zones, one of which leaks when other is on

Newbee who feels so lucky to have found this forum when searching EWC valve issues. I have 2 zones in the guest house with 2 MA-ND zone valves and a BMPlus 2000 Ver 1.3 controler. It was installed around 14 years ago and has worked without issue till now. I discovered that the main floor zone will ...