Search found 5 matches
- Wed Jun 09, 2010 12:43 pm
- Forum: Help and Advice
- Topic: No HVAC Operation
- Replies: 9
- Views: 15407
Re: No HVAC Operation
Hello Patrick. The 1 and 2 leads come directly from the transformer mounted to the unit adjacent to the Control Board. Low voltage connection (24V Power) R and C can be traced to the Control Board as well. R connected directly to the System Termination Block on the Control Board, C wire nut ...
- Wed Jun 09, 2010 9:55 am
- Forum: Help and Advice
- Topic: No HVAC Operation
- Replies: 9
- Views: 15407
Re: No HVAC Operation
This is the same transformer that feeds the Control Panel, no?
I confirmed voltage on that transformer to the Control Panel terminations 1 and 2.
I am not aware of a second transformer.
You are dealing with a homeowner here.
Is there another transformer that I cannot see?
I confirmed voltage on that transformer to the Control Panel terminations 1 and 2.
I am not aware of a second transformer.
You are dealing with a homeowner here.
Is there another transformer that I cannot see?
- Tue Jun 08, 2010 1:05 pm
- Forum: Help and Advice
- Topic: No HVAC Operation
- Replies: 9
- Views: 15407
Re: No HVAC Operation
Thanks for the assistance.
I checked across the common "C" of the Lennox Board to the System Output "R" as you suggested - No voltage.
Again, I appreciate the assistance.
Richard
I checked across the common "C" of the Lennox Board to the System Output "R" as you suggested - No voltage.
Again, I appreciate the assistance.
Richard
- Tue Jun 08, 2010 11:17 am
- Forum: Help and Advice
- Topic: No HVAC Operation
- Replies: 9
- Views: 15407
Re: No HVAC Operation
Patrick,
Just checked C to Y on the Zone 1 T-Stat with the thermostat calling.
Voltage @ 30.1V.
I suspect it is related to the output signal given I've no input to the Lennox Board...
Richard
Just checked C to Y on the Zone 1 T-Stat with the thermostat calling.
Voltage @ 30.1V.
I suspect it is related to the output signal given I've no input to the Lennox Board...
Richard
- Fri Jun 04, 2010 5:35 pm
- Forum: Help and Advice
- Topic: No HVAC Operation
- Replies: 9
- Views: 15407
No HVAC Operation
I have a EWC-ST-3E controlling a hot oil furnace and central air conditioning system - all Lennox equipment. Recently I commenced the seasonal change over from Heat to Cool when the system went down. The following morning, I removed the panel from the outside AC unit only to find that mice had taken ...