Search found 7 matches

by Glenn14
Fri Aug 05, 2016 3:07 pm
Forum: Help and Advice
Topic: Combining two zones
Replies: 3
Views: 4529

Re: Combining two zones

Actually, I changed it and jumped the 3 T-wires for the two zones instead. That seems to have fixed the issue and everything is working as it should.
by Glenn14
Wed Jul 27, 2016 1:07 pm
Forum: Help and Advice
Topic: Combining two zones
Replies: 3
Views: 4529

Re: Combining two zones

Should I have jumped the T-wires instead of the M-wires?
by Glenn14
Wed Jul 27, 2016 10:14 am
Forum: Help and Advice
Topic: Combining two zones
Replies: 3
Views: 4529

Combining two zones

I have a EWC OR-6 control panel. I wanted to combine two of my 4 zones, so I removed the thermostat wires to Zone 2 and jumped all of the M connections (M1, M2, M4, M5 and M6) across the Zones 1 and 2 in the panel. This seemed to work at first, but now I've noticed that both damper motors are runnin...
by Glenn14
Sun Feb 14, 2016 7:29 am
Forum: Help and Advice
Topic: How to diagnose zone damper problem
Replies: 1
Views: 3397

How to diagnose zone damper problem

One of the zone dampers in my system is not opening. The controller panel is an EWC-OR-6 Ultra Zone. Is there a way I can diagnose the problem -- would it be the damper motor or the zone relay? I do not have testing equipment. Is there another way to isolate the cause?
by Glenn14
Sun Feb 14, 2016 7:20 am
Forum: Help and Advice
Topic: Slide switch position
Replies: 1
Views: 3140

Slide switch position

The slide switches on my EWC-OR-6 Ultra Zone controller panel are all set to "O" (Open). Is this the typical setting? Intuitively, to me it seems like "C" would be the normal position. The description says: "In C position, the zone damper stays closed unless thermostat is ca...
by Glenn14
Wed Nov 04, 2015 9:57 am
Forum: Help and Advice
Topic: Where is C-wire
Replies: 2
Views: 4144

Re: Where is C-wire

I was hoping not to have to go that route. I realize the thermostat would not control the heat/cool/fan functions -- I would still use the master switch for that. Is there any chance of finding a suitable c-wire connection using the existing panel?

Thanks!
by Glenn14
Mon Nov 02, 2015 3:23 pm
Forum: Help and Advice
Topic: Where is C-wire
Replies: 2
Views: 4144

Where is C-wire

I have a EWC-OR-6 Ultra Zone controller panel (with 4 heating/cooling zones). I want to connect a Honeywell wifi thermostat but it requires a C-wire. I have run a spare wire from the thermostat to the zone controller, but can't figure out where to connect it (don't want to guess wrong). Honeywell sa...